Multiple BDR's

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts
  • top brake
    Automated Home Legend
    • Feb 2015
    • 826

    #31
    You need to bind the system using guided config and under stored hot water choose 2 X 2 port

    Under zoning config you do not need to control the heat demand. The heat demand is supplied as explained in previous post
    I work for Resideo, posts are personal and my own views.

    Comment

    • top brake
      Automated Home Legend
      • Feb 2015
      • 826

      #32
      Please do another drawing showing rooms in house and zones you want to create. Then we will need to arrange a call to talk you through
      I work for Resideo, posts are personal and my own views.

      Comment

      • top brake
        Automated Home Legend
        • Feb 2015
        • 826

        #33
        When you are binding zones you need to bind the radiator controllers as per the instruction manual. That's all. No binding to BDR91

        Evohome installation manual covered on page 14

        This is your biggest issue

        Originally posted by VvrooomM View Post
        I've been through the you learn, you suggested I drop the 8 rooms with rad controllers down to the zone level. I've reset and gone through guided config. It asks how many zones. I've got 8 rad controllers and one wireless stat for underfloor so selected 9. It then asks the remote sensor to be bound which has to be the rad controller, it then wants the zone valve which must mean BDR as there is nothing left. By the time I get to zone/room 4 the BDR shows red.
        I work for Resideo, posts are personal and my own views.

        Comment

        • top brake
          Automated Home Legend
          • Feb 2015
          • 826

          #34
          Finally your ufh zone needs to be added as a ZONE VALVE heating zone type using ADD ZONE. You can't do this in guided config. Has to be same heating zone type in guided config.
          I work for Resideo, posts are personal and my own views.

          Comment

          • VvrooomM
            Automated Home Sr Member

            • Dec 2015
            • 75

            #35
            Done all the above to best of my ability but wasted another half day of my life it seems. When I raise the UF temp, both the CH and UF BDR's illuminate green. Not the end of the world but means both bathroom rads are on whenever the UF is on which will be most of the day.

            Comment

            • top brake
              Automated Home Legend
              • Feb 2015
              • 826

              #36
              Originally posted by VvrooomM View Post
              Done all the above to best of my ability but wasted another half day of my life it seems. When I raise the UF temp, both the CH and UF BDR's illuminate green. Not the end of the world but means both bathroom rads are on whenever the UF is on which will be most of the day.
              That is what will happen. It is as intended. The CH BDR is at the system level.
              I work for Resideo, posts are personal and my own views.

              Comment

              • VvrooomM
                Automated Home Sr Member

                • Dec 2015
                • 75

                #37
                So I cannot control my UF independently of CH? Agreed that HR92 rads will not open unless asking for heat but my three standard rads (2 baths and WC) will be hot whenever UF is calling for heat.

                Comment

                • top brake
                  Automated Home Legend
                  • Feb 2015
                  • 826

                  #38
                  Your CH BDR is the master that fires the boiler.

                  So your uncontrolled radiators are on the primary circuit.

                  The only way to have your underfloor separated would be to have your underfloor heating on a separate controller.

                  Can you fit regular TRV to those radiators to stop overheating? This is what I have at home in the bathrooms. This is how I designed system so that when hot water comes on the bathrooms are heated in the summer.

                  Your other alternative is to fit HR92 to all radiators.

                  Hope this helps explain the logic.

                  Originally posted by VvrooomM View Post
                  So I cannot control my UF independently of CH? Agreed that HR92 rads will not open unless asking for heat but my three standard rads (2 baths and WC) will be hot whenever UF is calling for heat.
                  I work for Resideo, posts are personal and my own views.

                  Comment

                  • VvrooomM
                    Automated Home Sr Member

                    • Dec 2015
                    • 75

                    #39
                    Originally posted by top brake View Post
                    Your CH BDR is the master that fires the boiler.

                    So your uncontrolled radiators are on the primary circuit.

                    The only way to have your underfloor separated would be to have your underfloor heating on a separate controller.

                    Can you fit regular TRV to those radiators to stop overheating? This is what I have at home in the bathrooms. This is how I designed system so that when hot water comes on the bathrooms are heated in the summer.

                    Your other alternative is to fit HR92 to all radiators.

                    Hope this helps explain the logic.
                    How does your CH fire with HW???

                    I could fit TRV's or HR92's but I've always thought they were a bad idea in bathrooms as they get hot when in use naturally which in turn shuts down the rad as the room is hot.

                    I still have the odd snag to iron out though. Changing temp on evo base seems to have no effect of UF zone, changing on the wireless thermostat calls for heat and shows on evo base.

                    My CH BDR seems to stay on even when there are no rads calling for heat and UF BDR is off.

                    My UF manifold pump also still runs when UF off but CH running as its on the boiler switched live wire.

                    Comment

                    • VvrooomM
                      Automated Home Sr Member

                      • Dec 2015
                      • 75

                      #40
                      Thanks for your help, I work shifts so weekends don't exist for me, hope you're not wasting yours!! Guess you enjoy problem solving?!

                      Comment

                      • top brake
                        Automated Home Legend
                        • Feb 2015
                        • 826

                        #41
                        I don't have a CH Valve my system is installed as Fig 4 with boiler relay and the only 2 port valve is on the DHW

                        Make a note of all the niggles and I'll talk you through fixes

                        Originally posted by VvrooomM View Post
                        How does your CH fire with HW???

                        I could fit TRV's or HR92's but I've always thought they were a bad idea in bathrooms as they get hot when in use naturally which in turn shuts down the rad as the room is hot.

                        I still have the odd snag to iron out though. Changing temp on evo base seems to have no effect of UF zone, changing on the wireless thermostat calls for heat and shows on evo base.

                        My CH BDR seems to stay on even when there are no rads calling for heat and UF BDR is off.

                        My UF manifold pump also still runs when UF off but CH running as its on the boiler switched live wire.
                        I work for Resideo, posts are personal and my own views.

                        Comment

                        • top brake
                          Automated Home Legend
                          • Feb 2015
                          • 826

                          #42
                          I work for Honeywell but I'm on here of my own interest and to help where I can

                          Originally posted by VvrooomM View Post
                          Thanks for your help, I work shifts so weekends don't exist for me, hope you're not wasting yours!! Guess you enjoy problem solving?!
                          I work for Resideo, posts are personal and my own views.

                          Comment

                          • VvrooomM
                            Automated Home Sr Member

                            • Dec 2015
                            • 75

                            #43
                            Going to give this one last go to correct the errors you've highlighted. My UF BDR is wired as per fig 7, going to adjust the zone valve wiring hopefully. Are you suggesting I do not use grey (perm live) and orange as this is what you've described as hybrid. I understand the CH BDR will call for any heat as designed.

                            Can I use the orange zone valve switched wire to feed the live on my UF heating manifold pump so that it is only on when UF zone open? Rather than powered whenever CH is on. It is currently wired to the same orange switched live as CH.

                            Comment

                            • VvrooomM
                              Automated Home Sr Member

                              • Dec 2015
                              • 75

                              #44
                              If I can drop the orange and grey from UF , why is it needed for HW. Getting myself tied in knots again!!

                              Comment

                              • VvrooomM
                                Automated Home Sr Member

                                • Dec 2015
                                • 75

                                #45
                                Originally posted by top brake View Post
                                You need to bind the system using guided config and under stored hot water choose 2 X 2 port

                                Under zoning config you do not need to control the heat demand. The heat demand is supplied as explained in previous post
                                In an earlier post you suggested I should choose HW only valve, yet here you say 2x2 port.

                                With 2x2 port I receive HW actuator errors, with HW Only, I lose app control of the HW. LOSE LOSE?!

                                Comment