I have a Vaillant Ecotec VU 656/4 installed in 2017 an EvoHome Control System (Cylinder Stat, Rad valves) on an S-Plan System with BDR91 connecting to the HW and CH valves.
The boiler is operating in on/off mode connected via the 230v Terminal 3 and 4.
To try to take advantage of the boiler modulation, I have installed the VR33 module, wired to the OpenTherm Bridge (R8810A) connected to the EvoHome system.
I have placed jumpers between Terminals 3 and 4, as well as the 24V RT terminal 7 and 8.
The system recognises the VR33/OpentTherm control: D.90 = 1
However, the boiler stays in S.31: No heat requirement from eBUS controller (D.23 = 1 Heating on i.e. not summer mode), even though the system is calling for heating and/or hot water with valves open.
The VR33 installation instructions are not clear, but the green status LED on the VR33 board flashes (blips) every second. I'm unsure whether this is Flashes: Normal Function or Flashes Rapidly: No eBUS connection to the heat generator.
Has anyone come across this before and managed to resolve?
Thanks.
The boiler is operating in on/off mode connected via the 230v Terminal 3 and 4.
To try to take advantage of the boiler modulation, I have installed the VR33 module, wired to the OpenTherm Bridge (R8810A) connected to the EvoHome system.
I have placed jumpers between Terminals 3 and 4, as well as the 24V RT terminal 7 and 8.
The system recognises the VR33/OpentTherm control: D.90 = 1
However, the boiler stays in S.31: No heat requirement from eBUS controller (D.23 = 1 Heating on i.e. not summer mode), even though the system is calling for heating and/or hot water with valves open.
The VR33 installation instructions are not clear, but the green status LED on the VR33 board flashes (blips) every second. I'm unsure whether this is Flashes: Normal Function or Flashes Rapidly: No eBUS connection to the heat generator.
Has anyone come across this before and managed to resolve?