Evohome: Optimum Start Jankyness

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts
  • jweaver
    Automated Home Ninja

    • Jan 2023
    • 466

    Evohome: Optimum Start Jankyness

    My Evohome has been pretty much faultless.. But this season, it seems to be a little unreliable, specially regarding "Optimum Start".

    On Friday I noticed that the boiler had not fired.. And when I looked at the controller, none of the zones were calling for heat, even though they were way below the set point and there was only minutes to go before the schedule kicked in.. Sure enough a few minutes later it came to life, but "Optimum Start" did not trigger for any zones, so the temperature was way to low until I got up to heat.

    The next day was the opposite.. I woke up at 6am as I heard the boiler fire.. And when I looked several of the zones had come to life, 2.5 hours early (with the Orange Arrow) even though they were only 1.5 degree off the scheduled set point.

    The same thing happened this morning.. Again, the boiler fired really early and several of my zones were in "Optimum Start" 2 hours early with only a degree to go.

    Has anyone else seen this?
  • jweaver
    Automated Home Ninja

    • Jan 2023
    • 466

    #2
    Same again this morning, but a a different zone.. Schedule was for 23 degrees at 7am.. But heating woke up at 5:15, when room was at 22 degrees already..

    Comment

    • G4RHL
      Automated Home Legend

      • Jan 2015
      • 1699

      #3
      I gave up on optimum start many years ago. It did nothing and when it operated it came on far too early, often an hour too early. Just as easy to simply bring the start time for a setting forward by 10 minutes. Eventually I learned to stop playing, ensured the flow temperature was set to 60C, reduced the power of the boiler to it’s minimum and sat back letting Evohome do its stuff. It works better that way!

      Comment

      • jweaver
        Automated Home Ninja

        • Jan 2023
        • 466

        #4
        Originally posted by G4RHL View Post
        I gave up on optimum start many years ago. It did nothing and when it operated it came on far too early, often an hour too early. Just as easy to simply bring the start time for a setting forward by 10 minutes. Eventually I learned to stop playing, ensured the flow temperature was set to 60C, reduced the power of the boiler to it’s minimum and sat back letting Evohome do its stuff. It works better that way!
        I am starting to think that.. Its odd.. I fitted a Honeywell CM67 in my old house which also had "Optimum Start" and it was brilliant.. After a period of learning, it would bring the heating on at exactly the right time so it was up to temp by the schedule.. And that was getting on for 30 years ago.....

        You would think that after several decades it would be even better than it was then.. But it just seems to work randomly.

        Like you, I think I might switch it off and tweak the schedules to compensate.

        Thanks.
        Last edited by jweaver; 3 November 2026, 03:14 PM.

        Comment

        • philchillbill
          Automated Home Legend

          • Jan 2017
          • 1717

          #5
          Schedule-shifting in EvoControl is great for day-to-day tweaking schedules for multiple zones via a single UI-slider if your requirements vary from day to day. Give it a try seeing as how you use EvoControl anyway.

          Comment